Question for those who are electrically skilled (generator cord question)

The Best online firearms community in Louisiana.

Member Benefits:

  • Fewer Ads!
  • Discuss all aspects of firearm ownership
  • Discuss anti-gun legislation
  • Buy, sell, and trade in the classified section
  • Chat with Local gun shops, ranges, trainers & other businesses
  • Discover free outdoor shooting areas
  • View up to date on firearm-related events
  • Share photos & video with other members
  • ...and so much more!
  • fng

    Well-Known Member
    Nov 2, 2008
    492
    28
    St. Charles Parish
    I am looking ro run a generator about 80' from my inlet box..My current set up, I have a 30amp inlet box powing a 30 amp breaker in my panel with an interlock kit. I usually just put my generator on side of my house and connect my normal 12' 10/4 so cord from generator to box. Im looking to move my generator to another spot which will make it about 80' from generator to box, question is will an 80' run of 10/4 SO cord be ok ?? generator is 5500 watts and will almost never see that full load..
     

    Tboy

    Moving forward
    Jul 14, 2008
    1,672
    48
    Greenwell Springs
    There are several EI apps that’ll do it for you. You didn’t spec 110 or 220v AC.

    Edited to update photos. Had 70deg C selected on the last photos. Updated with F.
     

    Attachments

    • IMG_8329.jpeg
      IMG_8329.jpeg
      126.5 KB · Views: 11
    • IMG_8328.jpeg
      IMG_8328.jpeg
      130.3 KB · Views: 11